Viessmann Vitodens shuts down in the middle of the night.

Brand new boiler. The owner has to get out of bed, switch the mode from "DHW and Heating" to "Standby" and then back again to get the boiler to fire. Happens every night.
I checked the heating and DHW schedule (0:00-24:00 hrs.) and Economy Mode is off.
Viessmann tech. support is scratching their heads as am I. Does anyone have a clue?
8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour

Two btu per sq ft for degree difference for a slab

Comments

  • GW
    GW Member Posts: 4,832
    I'd be wanting a new control for the boiler, or whatever brain handles that function. Did you try a factory reset?
    Gary Wilson
    Wilson Services, Inc
    Northampton, MA
    gary@wilsonph.com
  • Robert O'Brien
    Robert O'Brien Member Posts: 3,563
    222 or 200?
    To learn more about this professional, click here to visit their ad in Find A Contractor.
  • Maybe a bad ground or neutral connection-even back at the service drop?--NBC
  • Yes, Gary: I thought of that after I left the job. That will be next.

    Robert: It's a 200-W, B2HB-35.

    Nicholas: Brilliant! But is that how a bad ground manifests itself?

    8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour

    Two btu per sq ft for degree difference for a slab
  • JUGHNE
    JUGHNE Member Posts: 11,279
    Maybe at night as the electric load on the neutral changes, pretty hard to analyze. Could be OK during the day but not at night. Just AWAG
  • I was just taking a stab in the dark as a result of others who have had problems from dirty power, (mostly from generators).
    I am no electrician, but I read a lot.—NBC
  • GW
    GW Member Posts: 4,832
    good call, any electricians here? i wonder what kind of instrumentation would be needed to have a data logger on the voltage and hertz
    Gary Wilson
    Wilson Services, Inc
    Northampton, MA
    gary@wilsonph.com
  • Paul Pollets
    Paul Pollets Member Posts: 3,663
    Possible bad board. Replace it if wiring or timer setting doesn't work correctly. Try setting the timer for operation from 12:10am-11:50pm. If the boiler won't work in the settings, replace the board.
  • Thanks, Paul. I'll give it a shot.