Boiler Relief Valve Testing Do you do it?
tested a water heater one after replacing the flex tubes going into it. the prv was completely stopped up with scale.0
Test where required by the boiler mfr. and the mfr of the PRV. Have a spare on hand with the threads prepped with PTFE/ dope. Hydronic boilers are required to have shutoffs on the supply and return. If not present, explain their absence is preventing techs from testing the PRV, which is a safety issue. With the system and TX tank isolated, you should be able to make a switch under low pressure and have a bucket to catch most of the spillage. Read ME's post. As one who provides product liability support I can assure you the opposition will nail you if you failed to test/ replace as needed and that is found to be the proximate cause of a loss. If they refuse, document and consider shutting the boiler down. If scared to do this, send a certified letter return receipt to the Fire Marshal and owner. You must document the defect, the hazard and the consequences for failure to correct.0