Mixing Valve Checks vs Heat Trap
nj6964
Member Posts: 22
I have an indirect water heater I’ve decided to increase its temp to 140 and add a Caleffi 521519 mixing valve (based on recommendations from HH). I see it comes with or without check valves. I was expecting to have to create a heat trap, but if the mixing valve has checks, do you still need a heat trap? Any advantages/disadvantages? Thanks!
0
Comments
-
Correct, you don't need a heat trap if you use a mixing valve with checks.
Advantage is you don't have to pipe the heat trap. Disadvantage is that check valves break.8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0 -
Thanks. So from a flow perspective, maybe better off piping the heat trap and not having the added flow restriction of the check valve?0
-
Unless your water pressure is below 30 psi, you don't need to worry about flow restriction.
If you have galvanized pipe anywhere in your house, go with the heat trap. Debris from the buildup and release of minerals in galvanized pipe can damage the check valves.8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0 -
No galvanized anywhere, comes in copper, goes to pex. I think I’ll make life easier and just use the check valves. Thanks!0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3K A-C, Heat Pumps & Refrigeration
- 50 Biomass
- 419 Carbon Monoxide Awareness
- 75 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 93 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 922 Plumbing
- 6.1K Radiant Heating
- 373 Solar
- 15K Strictly Steam
- 3.3K Thermostats and Controls
- 50 Water Quality
- 39 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements