Mixing Valve Checks vs Heat Trap
I have an indirect water heater I’ve decided to increase its temp to 140 and add a Caleffi 521519 mixing valve (based on recommendations from HH). I see it comes with or without check valves. I was expecting to have to create a heat trap, but if the mixing valve has checks, do you still need a heat trap? Any advantages/disadvantages? Thanks!
  • Correct, you don't need a heat trap if you use a mixing valve with checks.
    Advantage is you don't have to pipe the heat trap. Disadvantage is that check valves break.
  • Thanks. So from a flow perspective, maybe better off piping the heat trap and not having the added flow restriction of the check valve?
  • Unless your water pressure is below 30 psi, you don't need to worry about flow restriction.
    If you have galvanized pipe anywhere in your house, go with the heat trap. Debris from the buildup and release of minerals in galvanized pipe can damage the check valves.
  • No galvanized anywhere, comes in copper, goes to pex. I think I’ll make life easier and just use the check valves. Thanks!
