Effectiveness of copper finned tube
1) Considering that the finned tubes need air movement and an air space below the fins, how do you insulate?
2) Upstairs is a separate zone than downstairs (radiant tubing in the slab), but as you can imagine, this upstairs system heats both floors. Do you think removing this system and going with a product like Ultra-Fin would be better?
Two btu per sq ft for degree difference for a slab
Comments
-
I think you would want the element up in the bay, like UltraFin installs. Then a 4" air gap with 4-6" of insulation underneath.
Just getting rid of those bent nail hangers would be an improvement
On one Ultra Fin job we stapled bubble foil below it a few inches, then they spray foamed against that. It is a good way to seal the joist ends and rim joist with foam.
The copper tube is certainly a better conducted compared to thicker walled PEX in UF, it would be a quick performer. It's probably UltraFin times 10 with copper and much more fin surface.
Allow for expansion movement of course.
You certainly see some unique jobs out there. Those old hippie engineers.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream3 -
California Dreaming.
probably built in the 50s with the no plywood subfloor T & G run on a 450 -
Hot Rod: Diversity comes in many forms.
And yes on the better heat transfer of copper.
EBEBRATT-Ed: What gave it away? "Mid-century modern"? : )
So, if this were your house, would you leave it alone and cover it up with some ingenious insulation method or remove it all and install something like Ultra-Fin or heat transfer plates?8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0 -
I’ve brought in 10 companies and known have ever seen this type of radiant heat. I thought it was levitt system, but the last guy said it was a Venturi radiant heat system. Meaning it all
connects. So the problem is the ceiling was so frozen and busted, as we are fixing it’s spreading the busted pipes as water can move through. We don’t want to take anymore ceilings down, don’t even necessarily want ceiling heat, but it all connects I’m assuming to the pipes in the concrete first floor. When we put the 2 zones on, first and second floor, the water immediately goes to the leak areas, not even sure if the water is moving anywhere else. Kitchen ceiling leaking and second bedroom ceiling. I found some yellow valves. I’m thinking maybe if I find the ones to isolate the leaks, water will stop going to those specific rooms/area and maybe to the concrete floor area without and hear ducts. Companies recommending abandoning it and starting fresh with hydro heat loops in the AC units. Only problem is the first floor with no ducts, would be more invasive or install baseboards or mini splits. We don’t want either. No company really wants to touch it and just says it was luxury in the day but ancient and outdated and once u have busted pipes it’s only time the rest will bust. Feeling torn. Really want the radiant heat but no clue if this is even safe in the end or more busted pipes to come.
0 -
Tough to read this, but I think I got the gist. Still not sure if it is the same job as @Alan (California Radiant) Forbes job that started this discussion. either way, the fact that there are broken pipes involved... My advise is to start over with something more conventional. If you really want radiant heat, then you need to put something in the floor. Maybe adding 1-1/2" gypcrete pour over 3/8" tubing... or electric radiant heat under new tile.Nataliedipaola said:I’ve
brought inrequested estimates from 10 companies andknown have ever seenno one has ever seen this type of radiant heat.I thought it was levitt system, but the last guy said it was a Venturi radiant heat system. Meaning it allnot sure of the design name but there are lots of broken pipes,
connects. So the problem is the ceiling was so frozen and bustedas we are fixing it’s spreading the busted pipes as water can move through. We don’t want to take anymore ceilings down, don’t even necessarily want ceiling heat, but it all connects I’m assuming to the pipes in the concrete first floor. When we put the 2 zones on, first and second floor, the water immediately goes to the leak areas, not even sure if the water is moving anywhere else. Kitchen ceiling leaking and second bedroom ceiling. I found some yellow valves. I’m thinking maybe if I find the ones to isolate the leaks, water will stop going to those specific rooms/area and maybe to the concrete floor areawithout and hear ductswithout any heating ductwork. Companies recommending abandoning it and starting fresh with hydro heat loops in the AC units. Only problem is the first floor with no ducts, would be more invasive or install baseboards or mini splits. We don’t want either. No company really wants to touch it and just says it was luxury in the day but ancient and outdated and once u have busted pipes it’s only time the rest will bust. Feeling torn. Really want the radiant heat but no clue if this is even safe in the end or more busted pipes to come.
What is the first floor (the floor with no ductwork) construction type? Slab on grade or in basement? Is it a wood floor over framing as in the photo above? the floor construction will determine the most economical floor heat available.
Good luck.Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements