vents in the house

acl10
Member Posts: 349
I am on the 2nd floor. I have Hoffman 40s and Gorton 4 , 5 , 6s The hoffmans close but the Gortons keep hissing. Most are new and I checked all. so they are all in good condition. The pressure in the boiler is set at .5 on the pressurtrol.
0
Comments
-
whats the question?
"The bitter taste of a poor install lasts far longer than the JOY of the lowest price"0 -
Is that the way its supposed to be. I thought all the vents close at a certain point. The only ones that are closing are the very small Hoffman 40s does something have to modified0
-
The gortons are good vents but they have the tendency to hiss/spit as the pressure creeps up to the cut out. Part of it has to do with how the float comes up to close the vent. Gortons close at a lower temperature than the hoffmans. Also the hoffmans close with a positive click. These vents tend to be quiet until they close.
I like ventrite vents #1 and #11 the old dole 1a for a little more venting capacity.0
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 56 Biomass
- 423 Carbon Monoxide Awareness
- 104 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 103 Geothermal
- 159 Indoor-Air Quality
- 3.6K Oil Heating
- 69 Pipe Deterioration
- 941 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements