Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.

Gorton 1 hisses while the boiler is on a whole time. Is that the way its supposed to be?

acl10
acl10 Member Posts: 349
I had a ventrite 75 on one of the mains and it would close after a while. The Gorton 1 I replaced it with doesnt close and hisses a whole time. Is that the way its supposed to be? It has a much bigger hole then the Ventrite 75. When I turn it over and blow into t it closes so I know thats not the problem.

Comments

  • New England SteamWorks
    New England SteamWorks Member Posts: 1,525
    Nope. It should close. But a #1 is likely to small, and if your system is large enough, may be forced open. Let us know a little more about your set up.
    New England SteamWorks
    Service, Installation, & Restoration of Steam Heating Systems
    newenglandsteamworks.com