Chevron oil burner
hartmanb
Member Posts: 5
in Oil Heating
Hey guys, just bought a house, and I've got an old Chevron oil burner furnace. Worked great for about a week, then started tripping the motor protection. Popped the transformer up and the motor turns very stiff. Pulled it off and am looking for a replacement. However I can't find any info on this particular motor. Would like to think I can get one with the same specs, like rpm, voltage, rotation etc and it would work. But I don't want to buy one and have it not work. So a couple questions, this motor has 2 wires, and the thing is old, so guessing it's not a capacitive start. Can I install a capacitive start motor on this without a new control box? And if I get a motor with the same specs, can I expect it to work? Here's a pic of the side of the motor. Thanks for the help!
Brent
Brent
0
Comments
-
Looks like a standard 3450-RPM burner motor. But take a pic of the burner itself so we can be sure.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Agree with @Steamhead. Just ask for a 3450 burner motor at a local distributor.
I've never heard of Chevron Burner but it might be worth it to get the fan as well. And a coupling while your in there.
Put the coupling on the fuel pump side and try to spin the coupling clockwise. There should be some mention but not too much.
Can you post some pics of the Chevron?0 -
If the motor is on the right side, looking from the rear of the burner, its a standard motor, if it's on the left you would need motor that's reversible, but I doubt it's on the left.
You could also bump up (if it is a standard burner motor) to a PSC motor.
You may need a coupling too.
I'd bring the motor and the coupling over to the supply house, they'll give you the right stuff (if they sell to homeowners).
But when you're done, you'll need to do a combustion analysisThere was an error rendering this rich post.
0 -
Once i get home I can take some pics, and yeah from the rear, the motor spins clockwise. As well as put the coupler in the pump and see if it's tight. Thanks for the input!0
-
-
> @EBEBRATT-Ed said:
> It's probably a rebranded burner. I know we used to install "Texaco" burners. It was just a Beckett AF with red paint on it. But buying it from a Texaco distributor was cheaper than the local supply house
And everybody's favorite, the Shell head.0 -
-
-
Pics are missing..............All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
OK, I see them now- it's a Beckett AF. Pretty much any standard 3450-RPM, 1/7 HP motor will fit. Just make sure you get the fan lined up correctly, about the same as it is now, and do a combustion test when it's back together.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
I am also pretty sure it is a standard 3450 rpm burner motor, but I would double check the rpm's on the motor to make sure it is not rated at 1725. If the data plate on the motor can't be read, look at the fuel pump (on the left side) plate to see what its rpm rating is.
Then, just go to any heating place and tell them you need a burner motor for this rpm rating.
Rick1 -
Great thanks for the help! It is a 3450 rpm motor0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements