closely spaced tees

Question about closely spaced tees: is it ok to have larger spacing than the rule of 4XD or no more than 12" on closely spaced tees for primary/ secondary piping connections.
Existing : 3" primary and 2.5" secondary pipe and the tees are 15.5" center to center.
Long story short, I am working on getting prices together for replacing 25 yr old boilers and correct nearby piping (which I thought was incorrect due to spacing ). I asked the distributor (who will supply equipment) to come look at the job and piping (they like to be involved with planning of large jobs) and it blew my mind when the hydronic specialist from the distributor tells me that 15.5" spacing is fine and can be reused and not necessary to correct.
So I hit the books again, and could find nothing other than 4XD no more than 12" (Caleffi, taco, and Dan H. reference materials). Everything I have done, learned and was taught has made it difficult for me to accept that 15.5" space between tees is correct with no negative affect.
Can closely spaced tees be spaced further and how much is too far (especially if 12" is supposed to be max).
Thanks in advance


Comments

  • Gordy
    Gordy Member Posts: 9,546
    Is this copper.or iron piping? How much space is between the actual t fittings?
  • hot_rod
    hot_rod Member Posts: 22,120
    It is all about keeping the pressure drop between the tees as low as possible. It can never be 0, even 1" length of pipe has some pressure drop, depending on flow rate.

    Even with the tees close nippled together you would probably have 10"? branch to branch. 4D on 3" pipe is 12".

    Usually the secondary branches have a pump and a check, and I would add a check on the return also. So I doubt a few extra inches between the tees will cause problems.

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    DZoro
  • PM Home and Cabin Services
    PM Home and Cabin Services Member Posts: 23
    edited January 2018
    Thanks for the fast replies
    Piping is iron.
    It is a relief to hear others agree a few inches should not be a problem, makes for a simpler project.
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 15,517
    It will be fine. A few inches seldom matters
  • Tinman
    Tinman Member Posts: 2,808
    The smaller the gap, the better. Keep'm as close as possible.
    Steve Minnich
  • GW
    GW Member Posts: 4,692
    Many (15 or so) years ago it was 6x, then I’ve been seeing 4x for the last 5 or so years. Did someone move the cheese? Regardless it all works, unless you’re doing big and small gpm. Similar gpm seems like it won’t matter much
    Gary Wilson
    Wilson Services, Inc
    Northampton, MA
    gary@wilsonph.com
  • Tinman
    Tinman Member Posts: 2,808

    Steve Minnich
    Gordy
  • hot_rod
    hot_rod Member Posts: 22,120
    GW said:

    Many (15 or so) years ago it was 6x, then I’ve been seeing 4x for the last 5 or so years. Did someone move the cheese? Regardless it all works, unless you’re doing big and small gpm. Similar gpm seems like it won’t matter much

    Good point! Without running complicated calculations on every job I doubt we will reach a one dimension fits all answer.

    Putting ones hands on the take offs is a good indicator of how well the separation function is working.

    Checks are cheap and easy and near 100% assurance.
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • Tinman
    Tinman Member Posts: 2,808
    Siggy's first book came out about 20 years ago, didn't it?
    Steve Minnich
  • Gordy
    Gordy Member Posts: 9,546
    Always knew the 4 pipe diameters, 12” max. Never the 6pipe diameters. I suppose it depends on how the primary, secondary flows behave is the bottom line,
  • GW
    GW Member Posts: 4,692
    Ok I guess I dreamed it
    Gary Wilson
    Wilson Services, Inc
    Northampton, MA
    gary@wilsonph.com
  • Gordy
    Gordy Member Posts: 9,546
    NOT saying you dreamed it just didn’t remember coming a crossed it.