Uneven heating in some Cast Iron Radiators
hal1000
Member Posts: 8
in Gas Heating
I have an old 2 story home with a boiler and cast iron radiators. I only have 1 zone, but the supply splits up into two loops. I believe that the loops are not divided by floor, but by North half/South half. 3 of the radiators are not as hot as the others. I think that colder radiators are at the tail end of the loops. Curiously, the return pipe is slightly hotter than the 3 lukewarm radiators....
I have 1 circulator pump.
Any ideas?
Any ideas?
Is this a monoflow system? Can you post photos?Hydronics inspired homeowner with self-designed high efficiency low temperature baseboard system and professionally installed mod-con boiler with indirect DHW. My system design thread: http://forum.heatinghelp.com/discussion/154385
System Photo: https://us.v-cdn.net/5021738/uploads/FileUpload/79/451e1f19a1e5b345e0951fbe1ff6ca.jpg0 -
Can you use the shutoff valves on the hottest radiators to dial back some flow and allow more heat to travel to the farther radiators?Contact John "JohnNY" Cataneo, NYC Master Plumber, Lic 1784
Consulting & Troubleshooting
Heating in NYC or NJ.
Classes0 -
I believe it is a 2 pipe system.0
@JohnNY
Yes, I will try turning down the valves to the hottest radiator. This could possibly even out the radiators within that loop.
How do I control the flow if one loop is colder than the 2nd loop? There is one circulator with 0 zone valves. However, there are some shutoff valves for each loop.
Did the system work fine before and this is a new problem?
You think it's a two pipe system. Can you trace the piping in and out of each radiator and tell us if it's direct return or reverse return?
Direct return diagram...
https://insulation.org/io/wp-content/uploads/sites/3/2016/10/IO150205_01.jpg
Reverse return diagram...
https://insulation.org/io/wp-content/uploads/sites/3/2016/10/IO150205_02.jpg
What size are the main supply and return pipes? How many radiators on each loop? What is the length out and back for the furthest radiator in each loop?
Per your other thread about circulator pumps, what circulator is there now?
- 87.4K THE MAIN WALL
- 122 Chimneys & Flues
- 116 Geothermal
- 15.8K Strictly Steam
