Single wall heat exchangers
BobZmuda
Member Posts: 23
In 2015 Minnesota changed their code to allow single wall heat exchangers for DHW in boiler systems. There are some stipulations though such as a 30psi or lower relief valve on the boiler, the heat transfer medium should be potable water _or_ contain a fluid that has a toxicity class or rating of 1 according to some book published in 1984.
Apparently sentinel x100 meets this requirement BUT a local inspector is saying that no single wall heat exchangers can be used unless everything on the boiler side is rated for potable water. Pumps, 100 year old radiators, etc.
Also, you need some warning stickers.
IMO the UPC code is relying on the difference in pressure of the relief valves to prevent dangerous cross contamination. Because even if you meet the ridiculous standards of everything on the boiler side being rated for potable eventually the water you put in the boiler will become non potable after some time. I don't foresee anyone doing a daily flush of their boiler system to maintain potable water status.
Any thoughts? Help? lol. I'd like to be able to install combis or indirects if necessary.
Apparently sentinel x100 meets this requirement BUT a local inspector is saying that no single wall heat exchangers can be used unless everything on the boiler side is rated for potable water. Pumps, 100 year old radiators, etc.
Also, you need some warning stickers.
IMO the UPC code is relying on the difference in pressure of the relief valves to prevent dangerous cross contamination. Because even if you meet the ridiculous standards of everything on the boiler side being rated for potable eventually the water you put in the boiler will become non potable after some time. I don't foresee anyone doing a daily flush of their boiler system to maintain potable water status.
Any thoughts? Help? lol. I'd like to be able to install combis or indirects if necessary.
0
Comments
-
-
-
Sticky wicket. Bottom line, the field AHJ has the final say so, regardless of what the code says. IAPMO does have an "Ask the Inspector" section on their web site, but I doubt you'd get anyone to pony up an opinion on this hot potato.
I think a person has to say "Would I be comfortable drinking this water?" I think their biggest fear is not whats in the water now, but what HAS been (nitrates) in the water prior to this point in time. They used some seriously nasty chemicals, when and where they used chemicals.
Double walled heat exchangers in and of themselves are not too bad at thermal transfer. It's when you throw the "Positive leak detection" into the mix that quashes thermal efficiency. That air gap kills it.
METhere was an error rendering this rich post.
0
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 96 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 928 Plumbing
- 6.1K Radiant Heating
- 384 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements