Down fire Dunkirk Steamer 246B-6??? Need Advice.....have one cracked burner tube
Options
JUGHNE
Member Posts: 11,513
I have seen smaller versions of these with one manifold orifice opening with a solid plug, factory setup.
I have one burner with crack on far end burning badly.
There are 10 burners with 6 CI sections.
The end burners are not directly under the sections, rather that flame/heat is directed inward side ways by firebrick.
I was looking for opinions and ramifications of what to be wary of by plugging/capping off that end burner or maybe both end burners.
This is 525,000/420,000 BTUH. Clocked meter at 514,285 BTUH.
Connected EDR is 1218 X 240 = 292,320 and with 1.33 pick up needs 388,786 BTUH.
Plugging one burner would drop 10% giving 378,000 output.
Plugging two burners would drop 20% giving 336,000 output.
336,000 would give 15% pickup factor.
One pipe system, all piping is well insulated.
4" Header and 2 X 4" 6' risers.
Has anyone done this.......advice appreciated. Thanks.
I have one burner with crack on far end burning badly.
There are 10 burners with 6 CI sections.
The end burners are not directly under the sections, rather that flame/heat is directed inward side ways by firebrick.
I was looking for opinions and ramifications of what to be wary of by plugging/capping off that end burner or maybe both end burners.
This is 525,000/420,000 BTUH. Clocked meter at 514,285 BTUH.
Connected EDR is 1218 X 240 = 292,320 and with 1.33 pick up needs 388,786 BTUH.
Plugging one burner would drop 10% giving 378,000 output.
Plugging two burners would drop 20% giving 336,000 output.
336,000 would give 15% pickup factor.
One pipe system, all piping is well insulated.
4" Header and 2 X 4" 6' risers.
Has anyone done this.......advice appreciated. Thanks.
0
Comments
-
I would think that's something only Dunkirk can answer.0
-
We've done this in an emergency- remove the burner and orifice, and plug the orifice tapping using a standard plug of whatever pipe thread is used. Get the new burner and put everything back together.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0
Categories
- All Categories
- 87.3K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 429 Carbon Monoxide Awareness
- 120 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 115 Geothermal
- 166 Indoor-Air Quality
- 3.7K Oil Heating
- 77 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.7K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements