Steam Radiators Misbehaving
ewalls29
Member Posts: 26
I just moved into this 100 year old home (and in great condition for it's age). Came with a Galaxy GXHA-120 EDPZ previously installed. Here are some specs to give you an idea:
BTU/Hour: 120K
AFUE: 81.2
Fuel Type: Natural Gas
Steam Pipe Insulation: About 65% of the visible basement pipes are covered. I look in my crawlspaces and seems like all in there are covered (asbestos of course... )
Please note: this is a one-pipe steam system
THE ISSUE
I live in Pennsylvania and now that the weather is really starting to kick in (Highs in the teens and less), I have three radiators that are acting up
RADIATOR#1 (doorway entrance): Located on the first floor about 12 feet from furnace in the basement. Wouldn't warm up, so I gave it a little more slope and boom, nice and hot
RADIATOR#1 (1st floor living room): Located on the first floor about 18-22 feet from furnace. Same issue, gave it a little more slope and it fired up. There is a similar radiator in the same room without any issues.
RADIATOR#3 (1st floor bathroom): Located about 35-40 feet from furnace. Changed the airvent on this one and worked for about 3 weeks, then dead. Take the airvent off and only the first cell get hot. Put the vent back on, the whole thing goes cold. Not even an aggressive slope toward main did anything.
TROUBLESHOOTING
Apart from adding a slope toward the main on all three radiators, I have switched out variable airvents from other working radiators with the airvents of the radiators that don't work. The radiators that didn't work remained not working and the good rads continued to work despite the different airvent.
WEIRD BEHAVIOR
When I manually down the thermostat or the furnace turns of cause it reached temperature, the main pipe for RAD#1 and #2 suddenly gets got (just the pipe, no sections). But RAD#3 remains dead.
I'm eventually going to call an HVAC tech, but i've gotten a good handle on things and have been able to fix many issues already, but this is one that has stomped me. NOTE: My house is 3,680 sq ft. with 14 RADS. I can post the rad types if helpful (size etc..)
BTU/Hour: 120K
AFUE: 81.2
Fuel Type: Natural Gas
Steam Pipe Insulation: About 65% of the visible basement pipes are covered. I look in my crawlspaces and seems like all in there are covered (asbestos of course... )
Please note: this is a one-pipe steam system
THE ISSUE
I live in Pennsylvania and now that the weather is really starting to kick in (Highs in the teens and less), I have three radiators that are acting up
RADIATOR#1 (doorway entrance): Located on the first floor about 12 feet from furnace in the basement. Wouldn't warm up, so I gave it a little more slope and boom, nice and hot
RADIATOR#1 (1st floor living room): Located on the first floor about 18-22 feet from furnace. Same issue, gave it a little more slope and it fired up. There is a similar radiator in the same room without any issues.
RADIATOR#3 (1st floor bathroom): Located about 35-40 feet from furnace. Changed the airvent on this one and worked for about 3 weeks, then dead. Take the airvent off and only the first cell get hot. Put the vent back on, the whole thing goes cold. Not even an aggressive slope toward main did anything.
TROUBLESHOOTING
Apart from adding a slope toward the main on all three radiators, I have switched out variable airvents from other working radiators with the airvents of the radiators that don't work. The radiators that didn't work remained not working and the good rads continued to work despite the different airvent.
WEIRD BEHAVIOR
When I manually down the thermostat or the furnace turns of cause it reached temperature, the main pipe for RAD#1 and #2 suddenly gets got (just the pipe, no sections). But RAD#3 remains dead.
I'm eventually going to call an HVAC tech, but i've gotten a good handle on things and have been able to fix many issues already, but this is one that has stomped me. NOTE: My house is 3,680 sq ft. with 14 RADS. I can post the rad types if helpful (size etc..)
0
Comments
-
I'll ask the first most common question on here. What is your main venting like in the basement? Do you have any and where is it and how much? Pictures would help, also pictures of the boiler piping just because we like to see what is going on to make sure there aren't other issues.0
-
Based on what you said, it sounds like the pipes that run to those problem radiators either has no pitch back to the main, so water can drain out of them or they are pitched the wrong way or there is a sag in the middle of those runs, holding water.. Check that out. If they need more pitch, you can raise the entire radiator up, maybe a half inch then repitch them.0
-
Hi heating peeps. Sorry for the super duper late response but didn't see any notifications on this post!! I'm back here because I'm opening a new thread. But first, yes, tipping the radiators helped a ton!!! I essentially read hours and hours of how steam systems works and now understand a lot more than last year. And as for the main vent, its not installed. As I understand, you cannot balance a system without properly venting all the air, which leads me to my new post I am making. Thanks for your help on this!!.0
-
Putting a big mouth vent on the system will make a big difference.—NBC0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 50 Biomass
- 419 Carbon Monoxide Awareness
- 91 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 93 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 59 Pipe Deterioration
- 920 Plumbing
- 6.1K Radiant Heating
- 374 Solar
- 15K Strictly Steam
- 3.3K Thermostats and Controls
- 50 Water Quality
- 40 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements