Ever had a zone pulse or bounce occasionally?
Back zone of my house. A couple times a month I hear an engine idling in the distance. It’s my back zone pulsing or bouncing. Good x tank, 15-58 med speed. Changing anything quickly stops the phenomenon.
Thoughts? It’s strapped tight.
  • 15-58 got an IFC? Is there also a flow check in the circuit? What is your deltaT with it on low speed?
    hot_rod Posts: 28,511
    TRV on the circuit? sometimes they will pulse. Agree with the integral check valve in the circulator, it could be causing some pulsation on low flows.
  • Timco
    Timco Posts: 3,040
    Actually there is a FC in it and I put a spring check on returns to keep zones flow separated. Remove return spring check?
    The spring checks, were they hydronic type? Checks can have different "pop"or cracking pressure. Here is a common Conbraco soft seat check used for hydronics, notice the different pop pressures available.
    I think those checks in the circulator are somewhere between .35 and .50 psi crack. if you get too stiff of a spring the valve may hunt around causing the surge.
    Ideally when sizing a check use the flow rate not pipe size, often the check can be a few sizes smaller then the piping.
    Also know the Cv is with the check full open. If you have too much spring the check will possible rattle and also add some pressure drop, maybe turbulance if it in a partially open positions .
