30 psi gauge
JWise
Member Posts: 5
My pressure gauge sometimes reaches 5psi, why?
My cut-in is set at 0.5, with diff set to 1 on the dial. But the cut-out doesn't seem to happen until the psi gauge reaches 5psi. Is this ok ?
My cut-in is set at 0.5, with diff set to 1 on the dial. But the cut-out doesn't seem to happen until the psi gauge reaches 5psi. Is this ok ?
0
Comments
-
Could be gauge accuracy or pressuretrol accuracy, maybe plugged pigtail. There was a post on this issue recently.
Clean your pigtail, check ports on gauges to ensure they are free of dirt. Most recommend buying a low pressure gauge (0 to 3 or 0 to 5 psi) if you are serious about the diagnostics. Add that in addition to the 30 psi gauge.0 -
Is your control and gauge on the same pigtail?0
-
Put a 0-3 PSI gauge on there and see if it climbs. Re Calibrate the Pressuretrol if needed:
Inside the Pressuretrol, right below the micro switch, there is a pivot arm. At the end of that arm you will see a screw pin that is activated by the diaphragm at the bottom of the Pressuretrol. If you look very carefully at that screw pin, you will see it actually has a tiny (I mean tiny) hex head on it. It takes a .050 hex wrench and you can turn it clockwise (Towards the bottom of the Pressuretrol to decrease the Cut-out pressure or counter clockwise to increase the cut-out pressure (which none of us want to do but who knows, your Pressuretrol may be really screwed up!). Turn the power to the unit off first. You may find the first attempt to turn that screw a little bit stubborn (relatively speaking) because it has some Locktite on it but it does turn. Don't turn too much, a tiny fraction of a turn goes a long way towards getting it adjusted where you want it (maybe 1/32 inch turn to start with) . You may need to play with it to get it exactly where you want cut out to be.1 -
Could it be the gauge is wrong ? The pressure rises fairly quickly. Within minutes of firing up it hits 2 psi. Cuts out at 5.0
-
Certainly could be the gauge.0
-
-
I guess I don’t understand where pressure comes from in the system. My rads all heat up evenly and quickly. Just noticed the short cycling and the psi gauge raising quickly wasn’t “normal” after poking around these threads0
-
> @Neild5 said:
> The gouge could be bad, but if a new 0-3 pi gauge goes up that quickly you probably need to look at your main vents.
>
I just had this beauty placed0 -
If short cycling, it probably means:
- the boiler is over-sized and producing more steam than the connected radiation can condense
- the mains may not have enough (or any) vents which allows the back pressure to build as the steam tries to push the air out of the system
- the gauge is likely not defective
- You are using deep setbacks that require the boiler to run for extended periods to bring the house back up to temp0
Categories
- All Categories
- 86.4K THE MAIN WALL
- 3K A-C, Heat Pumps & Refrigeration
- 51 Biomass
- 419 Carbon Monoxide Awareness
- 91 Chimneys & Flues
- 1.9K Domestic Hot Water
- 5.4K Gas Heating
- 93 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 922 Plumbing
- 6.1K Radiant Heating
- 375 Solar
- 15K Strictly Steam
- 3.3K Thermostats and Controls
- 50 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 16 Recall Announcements