ECM pump recommendation

Torsten
Member Posts: 3
Finishing an Uponor-designed radiant heat system. Boiler is a Navien NCB-180E. Primary loop will use Navien's built-in pump. Secondary loop will have a single pump and I was wondering if someone could recommend a proper ECM pump for this application?
Following are more details and calculations from the Uponor design:
Following are more details and calculations from the Uponor design:
- Secondary loop separated by a 20 gallon buffer tank (HTP SSU-20B)
- Total RH Circuits: 16
- Total Manifolds: 3
- Total Zones: 7
- Smallest zone Head Loss: 0.9
- Total system Head Loss: 7.0
- Total Flow: 5.31
- Water Temp: 92.2
- Total Heating Load: 25,374 Btu/hr (Radiant Back Losses: 5,049 Btu/hr; Radiant Heating: 19,964 Btu/hr)
- First floor has in-slab tubing; second floor has heat transfer plates mounted to the sub-floor from below
0
Comments
-
The Grundfos ALpha2 may be a prefect fit for your needs, look at the pump curve chart...
https://www.supplyhouse.com/Grundfos-99163903-ALPHA2-15-55-F-Cast-Iron-Circulator-Pump-w-Terminal-Box
-1
Categories
- 120.2K All Categories
- 83.6K THE MAIN WALL
- 2.8K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 414 Carbon Monoxide Awareness
- 30 Chimneys & Flues
- 1.7K Domestic Hot Water
- 4.6K Gas Heating
- 114 Geothermal
- 152 Indoor-Air Quality
- 2.9K Oil Heating
- 49 Pipe Deterioration
- 736 Plumbing
- 5.2K Radiant Heating
- 357 Solar
- 13.8K Strictly Steam
- 3K Thermostats and Controls
- 50 Water Quality
- 36 Industry Classes
- 70 Job Opportunities
- 14 Recall Announcements