Riello misfiring
michelizzi
Member Posts: 3
in Oil Heating
I have a Columbia furnace with a Riello 40-F3 burner that had been working well since I bought this house. The other day I came back to a cold house and a locked out burner. I noticed the smell of burnt electronics and found a blown wire from the lockout switch and a popped capacitor, highlighted in the picture below.
Hoping that this was just a capacitor that gave up after 25 years or so of service, I ordered a replacement control box and switched over to the heat pump. When the new box showed up I installed it with the old CAD cell after checking it and going through the other voltage and resistance checks from the Riello troubleshooting chart. I bumped up the thermostat a few degrees and turned the furnace back on, then watched as it went all the way up to ignition, but cut out immediately after lighting. It would reignite every five seconds or so without locking out, but would never stay lit. I've posted a video to youtube just to make sure I'm not describing it incorrectly:
https://www.youtube.com/watch?v=2yVYTi2SPaU
Nothing in this system has changed that I could point to as a cause. Everything seems to check out when going through the troubleshooting chart. I'm used to being able to figure things out for the most part and an oil burner doesn't seem like rocket science (although I know that experience counts for a lot) but I'm at a loss here. Does anybody recognize these symptoms or have an idea of something else to check, or should I just suck it up and call in for service?
Thanks,
Mike
https://www.youtube.com/watch?v=2yVYTi2SPaUNothing in this system has changed that I could point to as a cause. Everything seems to check out when going through the troubleshooting chart. I'm used to being able to figure things out for the most part and an oil burner doesn't seem like rocket science (although I know that experience counts for a lot) but I'm at a loss here. Does anybody recognize these symptoms or have an idea of something else to check, or should I just suck it up and call in for service?
Thanks,
Mike
The tabs look like they should all be making good contact and the coil seems to check out (1-2: 1387 ohms, 2-8: 1.3 ohms).
Thanks for the suggestions!0 -
did you check the solenoid voltage didnt hear it snap open"The bitter taste of a poor install lasts far longer than the JOY of the lowest price"0
You may have a bad board, yes it can happen
Call a pro. This is not a DIY job. Where are you located? Have you tried the Find a Contractor page of this site?All Steamed Up, Inc.
Consulting0 -
First you'll need to properly purge the oil line. If everything checked out as you claim, it's either air in the oil line, or too much combustion air. But that's if everything really checks out.
Thanks for the replies everyone. When I tried purging the oil line I could not see any air coming out with it, but it's still acting the same. The solenoid voltage checked out when I looked at it (following along another post on here related to checking a Riello). I think I'm going to go ahead and call in a professional on this one.
Steamhead - I'm actually south of you in Fort Washington, MD. In the past my equipment was serviced by Southern MD Oil but I've had mixed results with them. I checked the contractor page for MD and found you and someone else in Baltimore. Is that too far for a service call?0
- 120 Geothermal