Caleffi 1" ZV Q

kcopp
kcopp Member Posts: 4,472
Anyone install the 6442 zone valves before.
Super high Cv.
Ball valve operation.
Union connections.
They look like they wire a bit different.
6 wires.
Can they be used in a Taco EXP ZV relay?
thanks...

Comments

  • hot_rod
    hot_rod Member Posts: 23,412
    The valve needs power to open, and power to close. It is not a spring return valve.
    It consumes no power when fully open or fully closed.

    6 wires are common, power open, power close, ground, 2-end switch

    Here are a few wiring options, as you need a double throw relay to operate it.

    The Caleffi single zone ZSR is a double pole, same wiring for the two way or three way valves.

    Add a RIB relay to a regular ZVR or ZSR.

    Or a 3 wire stat.

    The high Cv makes it popular with the pump and dump GEO guys & girls.
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • kcopp
    kcopp Member Posts: 4,472
    So I guess incorporating it into a Taco exp ZVC is not so straightforward.
  • hot_rod
    hot_rod Member Posts: 23,412
    Multiple zones I assume? One way is to add a RIB on every output
    of a typical multi zone relay box.

    Or use an individual relay, like this on every zone. The second set of contacts (dry) could call the boiler.

    The 120V jumper that powers the contacts of the relay needs to be removed.

    What kind of flow rates are you needing to zone?

    Our Z-one valves have a 7.5 cv. Here is what 10 gpm thru a 7.5 Cv valve looks like for pressure drop.

    But 10 gpm in a 3/4 copper tube would be around 7 fps velocity, a bit high for hydronics.

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • kcopp
    kcopp Member Posts: 4,472
    Yes. 3 zones. 2 radiant floor (staple up w/ plates) 1 DHW. Mod- con boiler.
    The exp relay prioritizes the hot water and has the boiler boost the output temp.
    I temporally hooked up a 1" Z-one valve until the 6442 arrived. 7 loops of 3/8 pert. 230' each loop. A wilo 21 drives the system.
    Somehow I thought it was a standard 4 wire zone valve.