use of copper convection baseboard with combi type boilers

Options
tombsr
tombsr Member Posts: 1
I have been a heating tech/installer/contractor since 1973 in New England area. I have recently been working in New York Queens area and have seen installation of fin tube Embassy baseboard with the closed fins facing up. I have seen this in normal boiler installs as well as with combi type boilers.
Is this a New york style of modified radiant heater? or is the installer brain dead??

Comments

  • kcopp
    kcopp Member Posts: 4,432
    Options
    He messed up. you will lose output by a lot...
    tombsr
  • Leon82
    Leon82 Member Posts: 684
    Options
    The air needs to enter the bottom and flow up thru the find and out the top opening to get published output.

    The air is going to swish around in there
    tombsrRich_49