oil burner won't fire
edracer
Member Posts: 9
Hi, I just replaced my tankless bypassed aquastat l8124a with a new l8148e. circulators come on, burner won't fire. Power to B1 & B2 connections is good, what's going on?
0
Comments
-
-
I assume the TT is jumped on you primary still?Serving Northern Maine HVAC & Controls. I burn wood, it smells good!0
-
Ummm isn't an L8148E for gas? 24v to burner circuit and you need 120v.
https://customer.honeywell.com/resources/Techlit/TechLitDocuments/60-0000s/60-2278.pdfThere was an error rendering this rich post.
1 -
Shows 28 acv when checking at b1 & b2
Not sure what jumping the tt means?0 -
Looks like 28 in the control as well?0
-
Idk plumbing supply place sold it to me?0
-
Thanks STEVEusaPA, that was the problem! They sold me wrong one. New one in, three heat is on!! Thanks all0
-
You got lucky it wasn't the other way around, sending 120 to a gas valve.
There was an error rendering this rich post.
0 -
/\
how bad could that have gotten?
cook the gas valve ?
or bigger kaboom ?known to beat dead horses0 -
Unfortunately you have to double check even at a plumbing store.
I saw the owner tell his worker to get a natural gas water heater. And then told him he would be fired if he brought a propane unit. So how many times has he messed that up.0 -
another question for you guys. upstairs thermostat calling for heat. circulator comes on, oil burner doesn't fire. only fires when downstairs thermostat is calling for heat?0
-
Could be wired wrong, or could simply be the boiler is up to the high limit, and the aquastat is holding off firing the burner.
Can you post a sketch on how you have it wired?There was an error rendering this rich post.
0 -
no changes to wiring, it used to work fine. there is a relay before the aquastat tstats, & line in come through it. boiler temp is below by 90 plus degrees?0
-
Do you have terminals zc and zr on the new control, we're they used on the old? 8124 and 8148 are different controls.0
-
-
You went from an aquastat that maintains temp to a high limit only, cold start. The first floor zone is connected to TT in the aquastat so if fires to limit and runs that circ on a heat call. Nothing on the switching relay for the upstairs zone is telling the burner, "hey, I need heat. It will run the circ only. You need to utilize ZR,ZC. What model is the switching relay for the upstairs ?0
-
wires I meant to type wires!0
-
HVACNUT got what I didn't feel like typing. The supply house still didn't sell you what you needed. When you use a different control you have to know what the previous control strategy was, and what you have to do to compensate. Easier to just replace like with like.0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements