Steam boiler
jameshannon
Member Posts: 1
in Gas Heating
I have a steam boiler with the new auto feed System keeps on filling up with water and leaking out the steam vents Any ideas what could be the problem
0
Comments
-
Sometimes the feeder doesn’t close properly. There should be an isolation valve before the feeder that you can shut. Either replace the feeder (with hydro level VXT only) or do away with it completely. You want to minimize how often the boiler feeds so unless you understand that, a water feeder can be a silent killer.0
-
need pictures. Is the boiler overfilling with water? Or is steam pushing water out the vents. Look at the gage glass.
Shut off the water drain the boiler down to normal (1/2 glass)
Could be a bad low water control operating the feeder. Need more information0 -
Brillant phraseology @Danny Scully !Danny Scully said:a water feeder can be a silent killer.
Permission to plagiarize?
Never fill auto without a VXT...
New England SteamWorks
Service, Installation, & Restoration of Steam Heating Systems
newenglandsteamworks.com0 -
Of course @New England SteamWorks, we’re steam brothers. What’s mine is yours!0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements