Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.

condonsate return lines

Options
bean
bean Member Posts: 34
I would like to know weather or not my condonsate return pump and piping needs to be sch.40 or 80?(low pressure heating steam)?

Comments

  • JUGHNE
    JUGHNE Member Posts: 11,062
    Options
    Sch 40 would be most common, 80 if you want to pay for it.
    40 might outlast the pump itself.
    Is this buried at all?
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 15,544
    Options
    Don't know what the price difference is.

    Schedule 40 in a residence will probably outlast you, unless you have excessive make up water or something funny going on. I have never seen schedule 80 used in a house and have seen many old, old systems where 40 held up well on steam heating systems

    Schedule 80 is usually used in commercial, industrial, schools, hospitals, manufacturing etc. These larger systems tend to have more leaks, use steam for process and generally have larger make up water requirements. as a result the condensate is more acidic so schedule 80 is used
    New England SteamWorks
  • MilanD
    MilanD Member Posts: 1,160
    Options
    Given my experience, anything after the pump will only benefit from sch. 80. Run shouldn't be too long and cost will be less than 100 bucks. Do it.

    I just posted about this.

    Milan