1 of 2 pumps turning off.
SeanBeans
Member Posts: 520
my site manager is having a problem with his navien boiler system.
he has 2 zones.. both controlled by pumps.heres the scenario.
1. the upstairs zone is calling for heat and working fine.
2. when the downstairs zone thermostat is set for heating it turns on.
3. but when the downstairs turns on it kills power to the top floor.
I don't have pictures at the moment.
It is hot water baseboard.
controlled by taco control board
what other information would you need to diagnose the problem?
he has 2 zones.. both controlled by pumps.heres the scenario.
1. the upstairs zone is calling for heat and working fine.
2. when the downstairs zone thermostat is set for heating it turns on.
3. but when the downstairs turns on it kills power to the top floor.
I don't have pictures at the moment.
It is hot water baseboard.
controlled by taco control board
what other information would you need to diagnose the problem?
0
Comments
-
Sounds like the priority setting is turned on for the downstairs zone.
the priority setting is typically reserved for DHW loads like an indirect tank. It will turn off all other zones until the demand for heat is satisfied and then turn on the other zones.
On the Taco SR panels or ZVC panels, the last zone on the controller is this priority zone. Just to the right of that terminal inside the controller is an on/off switch.
Switch it to off when you do not want priority.
Dave H.Dave Holdorf
Technical Training Manager - East
Taco Comfort Solutions
1
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements