Steam main check valve
Weil
Member Posts: 23
Gentlemen,
Can anybody tell me the purpose of a check valve in the main steam supply off of a 175 HP low pressure steam heating boiler? Below is picture. 80 year old government building. Not sure if it was a vacuum system but it is two pipe. Stockholm 12C is model #. Engineer wants it removed. I want to confirm its purpose first.
Can anybody tell me the purpose of a check valve in the main steam supply off of a 175 HP low pressure steam heating boiler? Below is picture. 80 year old government building. Not sure if it was a vacuum system but it is two pipe. Stockholm 12C is model #. Engineer wants it removed. I want to confirm its purpose first.
0
Comments
-
Are there or were there two boilers in that building? If so, the check was probably there so steam wouldn't back into the inactive boiler.
And what's that pipe coming off the bottom of the check?All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
I doesn't look like it goes anywhere. It looks like that gate is the end of the line. Or the beginning of an abandoned run. I don't see any piping connected to that gate valve. If that's right that whole run could be removed and capped down by the boiler. Maybe?Miss Hall's School service mechanic, greenhouse manager,teacher and dog walker0
-
I agree with Steamhead.Retired and loving it.0
-
I'd guess the pipe coming off the bottom is a support. I agree with @Steamhead as well.0
-
You do not need a check valve unless you have two boilers or two sources of steam such as district steam and a back-up boiler.
High pressure steam boilers in battery (two or more ) require two stop valves in series on each boiler as well as a check valve on each boiler. It is common procedure to use 1 stop valve and 1 non-return valve (which is a combination stop valve and check valve in one body) There is also supposed to be a manual drain valve between the two stop valves (usually 3/4")
In some circumstances the inspectors may allow the extra valves to be omitted IF the boilers do not have a manhole on the boiler (no one can crawl inside)
Valves are required so one boiler can be safely worked on while the other one continues to operate
In most locations HP steam is inspected by the state or an ASME certified boiler inspector.
I wouldn't alter anything without checking with the inspector0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 89 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements