Domestic Hot Water Recirculation with a mixing valve
Bob Gagnon plumbing and heating
Member Posts: 1,373
Does anyone have a diagram of how to pipe a recirc line with a thermostatic Honeywell mixing valve? It in New Hampshire and I can run 140 degree water to the system, maybe I don't need the mixing valve? I can't put mixing valves at point of use.
Thanks, Bob Gagnon
Thanks, Bob Gagnon
To learn more about this professional, click here to visit their ad in Find A Contractor.
0
Comments
-
Hmmm, I'd be surprised if the plumbing code allows 140F to the faucet, but I don't know the exact application. In some commercial jobs high temperature is allowed, maybe required for some dishwashing or sanitizing applications.
A point of use valve at every HW connection may be and acceptable option?
Here is a drawing for the correct way to pipe record thru a mixing valve. The crossover balance valve is crucial to prevent temperature droop or creep in the recirc loop.
Idronics11 is an issue dedicated to DHW production and recirculation.
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream2 -
Thanks for the quick response Hot Rod, I'll go with the mixing valve, I like that diagram. Should I put an aquastat in there, or just run it continuous?To learn more about this professional, click here to visit their ad in Find A Contractor.0
-
Sure, an aqua stat and or timer, or one of the Smart recirc pumps that learn usage trends.
The very best thing for recirc is insulating the entire loop. Then you have the most efficient system.
I've heard California requires recirc on any system longer that 100' and they also require 1" insulation!Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Thanks for all the good info Hot Rod, one last thing. They are boxing I the hot, cold and recirc line, is there any reason why they couldn't insulate around the pipes with fiberglass, rather than insulating the individual pipes?To learn more about this professional, click here to visit their ad in Find A Contractor.0
-
If the insulated box enclosure has both H&C running along side one another, will the cold line sweat? The hot may heat up that space and cause condensation? Don't know for sure.
At DHW temperatures, even the less expensive foam pipe insulation is fine, doesn't need to be Armaflex like refrigeration lines use.
I don't know how much tube you have to insulate, but it may be money well spent.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream1
Categories
- All Categories
- 86.4K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 91 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 921 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 15K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements