New Boiler Return Connection
Albie
Member Posts: 9
Hi to all,
I have an old hot water heating system consisting of a 1-1/4" supply and return loop with diverting tees with 1/2" supply/return to/from each heater. I want to install a new Buderus boiler but noticed the return connection on the boiler is only 1". Q. any problem with reducing the size of my return connection at the boiler?. A little background about myself, I'm an old geezer from the UK and was a Plumber for many years and have installed a few boilers in my time but I can't wrap my head around this little conundrum. Seems like there would be a bottle neck.
Thank you for any help.
I have an old hot water heating system consisting of a 1-1/4" supply and return loop with diverting tees with 1/2" supply/return to/from each heater. I want to install a new Buderus boiler but noticed the return connection on the boiler is only 1". Q. any problem with reducing the size of my return connection at the boiler?. A little background about myself, I'm an old geezer from the UK and was a Plumber for many years and have installed a few boilers in my time but I can't wrap my head around this little conundrum. Seems like there would be a bottle neck.
Thank you for any help.
0
Comments
-
The quick answer...the size of the pipe determines how much heat energy you can flow. What size boiler?
Typically a 1" pipe will carry 12 gpm, so 120,000 BTU/hrBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
I presume the boiler is the G115.
That "bottleneck" is there to prevent thermal shock.
You're fine in that application, just reduce it at the boiler. Don't use a bushing. Use a reducer coupling.
Sounds like it's a mono flo piping system, so DON'T reverse the supply and return.
Are you going to use the 2107 Logamatic?
You didn't say where your located (still the U.K.?), but most states in the northeast require a low water cutoff, if you didn't already know.1 -
Thanks for your answers. And yes it's the G115 boiler I'm looking at the heat load is only about 50,000 btu with a indirect water heater. I'm in the USA now and am aware of the low water cut off. Not sure if I'm going to use the logamatic yet still researching it, pretty expensive.0
-
It certainly isn't cheap, but we'll worth it IMO.0
-
-
All your comments have been a great help and as they say in Aussie land "Good on ya Mates"0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements