Caleffi & Uponor manifold orientation
roundrightfarm
Member Posts: 54
I'm looking for manifolds for a 19 loop home-run hydronic system.
The boiler room is in the basement and all piping will go up from there. Both Caleffi and Uponor have flow/balancing devices,which I definitely want, but everything in the manuals shows the manifolds mounted with the piping headed in a downward direction.
Is the orientation of these manifold important in order for the flow meters to work properly? It would be annoying to have to put a 180 degree turn in all 38 pipes.
The boiler room is in the basement and all piping will go up from there. Both Caleffi and Uponor have flow/balancing devices,which I definitely want, but everything in the manuals shows the manifolds mounted with the piping headed in a downward direction.
Is the orientation of these manifold important in order for the flow meters to work properly? It would be annoying to have to put a 180 degree turn in all 38 pipes.
0
Comments
-
Good practice to have the flow meters up, plus if there's going to be loop actuators, you don't want them upside down. Bring the loop leaders down and up into manifolds.0
-
If you can put a wall up and drop the loops behind them, then up in front and into the manifolds. I've used (and I can't remember the name) 2 of those purple (Watts?) guides that make and form a 90° loop instead of attaching elbows, but you are still going to have a lot of pipe loops.
I have seen them upside down, and flat (under a floor), I'm sure they would be ok that way tooThere was an error rendering this rich post.
0 -
This system will not have electronic actuators, the loop[s will be controlled by TRVs on the radiators in each room0
-
The Caleffi manifolds can be ordered inverted. Flow indicators are spring loaded and work upside down. Actuators are fine upside down also except for chilled water
Actually some models of our actuators Are hermetically sealed for inverted chilled water
Manifolds could be vertical alsoBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
> @hot_rod said:
> The Caleffi manifolds can be ordered inverted. Flow indicators are spring loaded and work upside down. Actuators are fine upside down also except for chilled water
>
> Actually some models of our actuators Are hermetically sealed for inverted chilled water
>
> Manifolds could be vertical also
Can I buy regular S1 manifold and convert to inverted?Thank you,
Hiren Patel0 -
You would need to switch the air vent and drain valve if you invert the standard S1. We assemble and pressure test all the manifolds in Milwaukee. if you disassemble and change things, you lose that assurance of the pressure test.hcpatel78 said:> @hot_rod said:
> The Caleffi manifolds can be ordered inverted. Flow indicators are spring loaded and work upside down. Actuators are fine upside down also except for chilled water
>
> Actually some models of our actuators Are hermetically sealed for inverted chilled water
>
> Manifolds could be vertical also
Can I buy regular S1 manifold and convert to inverted?
I think those parts are installed with Loctite, it may not be easy to switch in the field.
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0
Categories
- All Categories
- 85.9K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 420 Carbon Monoxide Awareness
- 78 Chimneys & Flues
- 1.9K Domestic Hot Water
- 5.2K Gas Heating
- 94 Geothermal
- 154 Indoor-Air Quality
- 3.3K Oil Heating
- 59 Pipe Deterioration
- 884 Plumbing
- 5.9K Radiant Heating
- 377 Solar
- 14.6K Strictly Steam
- 3.2K Thermostats and Controls
- 51 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements