Zv valve ghost flow
kcopp
Member Posts: 4,491
Anyone ever had a problem w/ ghost flow in a system w/ the Taco 571 zone valves? I have a system where this appears to be the case. I have exercised the plunger to make sure nothing is stuck and changed out the ZV head.
0
Comments
-
one or two over the years..0
-
Good morning
The 571 heat motor zone valve is a fail closed valve, so not likely to have ghost flow. However, it has a maximum shut off head of approximately 60 ft/hd, so if your system pump differential pressure is greater than shut off head, it will allow flow through?
Try taking the head off, and see if the pipe gets hot on both sides of valve. You could have a faulty thermostat too. If it’s a perpetual demand, the valve will stay open. Not too much more that can go wrong with 571 staple valve.
Joe Mattiello
N. E. Regional Manger, Commercial Products
Taco Comfort Solutions0 -
with any valve it is possible to get debris stuck in the valve mechanism that could cause "leakage"Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 96 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 928 Plumbing
- 6.1K Radiant Heating
- 384 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 42 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements