Used motor oil boiler.
Harvey Ramer
Member Posts: 2,261
I'm looking at a used motor oil boiler replacement. I don't deal with many so I'm wondering what brand is the best, or the most troublefree.
0
Comments
-
My limited experience and advice would be to only order one from a place that's nearby or has a factory rep nearby. I'm in Philly and I had a customer who ordered one from California. It was a nightmare to get parts and to address a warranty issue. Had to bring a welder in to fix the heat exchanger. They take a beating so the more filtration the better.
There was an error rendering this rich post.
1 -
-
I thought Clean Burn use to be out of PA?
I installed maybe 6 CBs over the year. They work best with a buffer tank, and post purge, especially if you start zoning them much.
If the combustion chamber fills with ash they tend to over shoot temperature as the ash holds some heat.
They need to be maintained and cleaned fairly frequently depending on the quality of the oil. Make sure the owner has the ability to maintain them. Ash removal and cleaning isn't a pleasant job.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream2 -
DANGER WILL ROBINSON, DANGER... you want a "Used Motor Oil" boiler, because it is illegal to burn WASTE oil (Brought to my attention by a Used Motor Oil Burner manufacturer who was compatible with Buderus 3 pass boilers) And as others have noted, these things require regular maintenance. I worked on two of them at a local concrete pumping facility, and they HATED doing the maintenance because it was SO dirty. And the good Lord knows what all was in the oil. It was hydraulic oil, gear case oil, engine oil and transmission fluid.
What happened to the first one?
METhere was an error rendering this rich post.
0 -
That's weird. One word makes all the difference. But hey, who am I to judge Thanks for the tidbit though. It could save a person from some unwanted attention.
The old one was installed in a radiant slab application, with no anti condensation protection. The flue tubes rotted and one now has a pinhole.
The latest word from the owner is that they are going to have the boiler retubed and then let me replumb it to my satisfaction.-1 -
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements