Steam Boiler Leaks O2 pitting
RayWohlfarth
Member Posts: 1,656
I am seeing a disturbing trend of O2 pitting inside low pressure steam boilers. One vertical fire tube boiler was only 2 1/2 years old and the customer has a water treatment program using a sulfite treatment. Another was a 9 month old horizontal water tube without treatment but used a softener. A two year old cast iron sectional without treatment had a leak just under the water line. I am not sure what the cause is. Some believe it is because of fracking and there is something in the water while others think it is chlorides in the water. I have spoken to water treatment experts and they are saying we need increase the sulfites. Are you seeing this trend?
Ray Wohlfarth
Boiler Lessons
Boiler Lessons
0
Comments
-
We are seeing water quality issues in ALL types of boilers. Check TDS, hardness and ph at every jobsite, with fairly inexpensive meters.RayWohlfarth said:I am seeing a disturbing trend of O2 pitting inside low pressure steam boilers. One vertical fire tube boiler was only 2 1/2 years old and the customer has a water treatment program using a sulfite treatment. Another was a 9 month old horizontal water tube without treatment but used a softener. A two year old cast iron sectional without treatment had a leak just under the water line. I am not sure what the cause is. Some believe it is because of fracking and there is something in the water while others think it is chlorides in the water. I have spoken to water treatment experts and they are saying we need increase the sulfites. Are you seeing this trend?
More analysis would involve a sample to a specialist.
Steam boilers have a bit different water spec, find their recommendations in the installation manual.
Most all of the chemical manufacturers will test water and make a suggestion for treatment, here is an example from Rhomar.
I agree the stuff we are putting into and onto the ground, as well as new chemicals that water providers use are creating more and different issues with piping and boilers.
I think we all need to start paying more attention to what goes in the systems,as well as a good cleaning procedure before filling.
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
-
What ppm of excess SO3 are they keeping in their boilers? Are the boilers on line all the time, or are they shut down on weekends/etc? I've seen some older boilers that are infrequently used with corrosion issues due to not enough treatment (phosphate and pH too low, so the steel doesn't have a chance to get it's protective magnetite coating).0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements