I have a customer with a steam boiler that is about 5 years old, the top left of the cast iron rotted out and needs to be replaced. I have a couple of thoughts I'd like your opinion on.
1) I sized the boiler to the connected load to the I could and came up with 250 sqft of edr. The existing boiler(IN5) is rated for 358 sqrft of edr. I would like to drop down to an IN4 which is rated for 271 sqft of edr, but I'm not 100% sure of the load I came up with. What size would you go with?
2) The existing boiler has only one 2" riser, I'm going to install two 2" with a drop header. Do you think the single riser could cause the boiler section to fail? The leak in the section is near where the second tap is.
I attached a couple of pix.
Thanks for your input.
0
Comments
-
1. Verify your connected EDR.
2. Not likely the single riser caused the rot. More likely the addition of a lot of fresh water or the quality of the water. Both need to be investigated.0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 918 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements