Newly installed

SeanBeans
SeanBeans Member Posts: 520
When you dont know how to get a 3 inch elbow off...

Comments

  • SeanBeans
    SeanBeans Member Posts: 520

  • Fred
    Fred Member Posts: 8,542
    I would say "When you don't know how to properly install a steam boiler".
    Paul S_3
  • Steamhead
    Steamhead Member Posts: 17,314
    edited March 2017
    Fred said:

    I would say "When you don't know how to properly install a steam boiler".

    I'll second that. That guy didn't read the manual. He reduced the 2-1/2" steam outlet to 2" with a bushing, which is a big no-no on a Dunkirk boiler.

    Then there is a concentric reducer on the header before the elbow to the equalizer. This will trap water in the header.

    This will produce wet steam, reduced efficiency and possibly banging.
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • Tinman
    Tinman Member Posts: 2,808
    A tubing cutter would have eliminated that 3" el in about 2 minutes.