Baxi luna 310
Steve_210
Member Posts: 647
in Gas Heating
Changed main board and air switch on this Two to three weeks ago.
It is not used for hot water
If I jump out of the micro switch assembly on the pressure differential, Pump starts fan proves and boiler fires I'm tricking the boiler into thinking there's a call for hot water and I get heat no problem but obviously I can't leave it like this
There is no external thermostat, jumper appears to be correct but I cannot get a call for heat pump does not even start.
I have the manual
Any advise
It is not used for hot water
If I jump out of the micro switch assembly on the pressure differential, Pump starts fan proves and boiler fires I'm tricking the boiler into thinking there's a call for hot water and I get heat no problem but obviously I can't leave it like this
There is no external thermostat, jumper appears to be correct but I cannot get a call for heat pump does not even start.
I have the manual
Any advise
0
Comments
-
The TT on Baxi 310FI uses 120V make sure you have wire rated for that and if you are running a single zone you need a relay to drop the 120v power from hitting your t stat. Also try putting a jumper on M block 1&2 to see if boiler fires up and when you installed new PSB board did you put brown jumper back in on I think it is A3 set of pins??0
-
0 -
Thanks Dave This unit looks a bit different the thermostat jumper is between four and six on a separate board
I did try jumping out 1&2 last night nothing
Small board has 110 coming in but no 24 on the thermostat side
I tried running separate power supply to the pump as a temporary measure but the pump light was flashing, put everything back together and it worked for a while and now has gone down again almost sure the small board needs to be replaced.0 -
Pull off small board and put back brown jumper and try 1&2 again if that work might be faster to get a single relay box. Also check pump wire to make sure its not kinked so when you put up panel it brakes circuit.0
-
Thanks pretty sure the pump wire is OK because it works when I create a dummy call for hot water
Well Troy what you said0 -
A friend of mine had a small board we changed it out solved the problem thanks for your help especially on a Sunday.0
-
No problem0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements