Sight Glass Slowly Refills
Frelee
Member Posts: 6
Hi all,
Starting about a month ago, the water level in the sight glass on my steam boiler has been slowly creeping upwards. About an inch every few days or so. I would drain it down via the valve at the bottom of the boiler to an acceptable level and after a few days, it would creep back up. Since the water is draining, I'm assuming that there's no blockages in the glass.
Even though the auto-feeder has not been kicking in, I've tried shutting off the valve to that pipe to test for a leak. That wasn't it. It leaves the only possible culprit to be the manual feeder is slowly leaking water. Am I correct or is there a possible third source of water?
Also, the water level is about 60% of the glass. After recently draining the system to replace a leaky return pipe, 1/2 the water in sight glass is brown. Should it not settle down or clear out as I'm draining down the water level?
Thanks for your comments in advance.
Starting about a month ago, the water level in the sight glass on my steam boiler has been slowly creeping upwards. About an inch every few days or so. I would drain it down via the valve at the bottom of the boiler to an acceptable level and after a few days, it would creep back up. Since the water is draining, I'm assuming that there's no blockages in the glass.
Even though the auto-feeder has not been kicking in, I've tried shutting off the valve to that pipe to test for a leak. That wasn't it. It leaves the only possible culprit to be the manual feeder is slowly leaking water. Am I correct or is there a possible third source of water?
Also, the water level is about 60% of the glass. After recently draining the system to replace a leaky return pipe, 1/2 the water in sight glass is brown. Should it not settle down or clear out as I'm draining down the water level?
Thanks for your comments in advance.
0
Comments
-
Does your boiler have an insert coil that heats your domestic water for showers, etc?0
-
No it does not, I have a separate boiler to heat water for showers and faucets.0
-
Can you post pictures of your boiler to show the feeder and all valves involved for it?0
-
Ok, will do it tonight. Thank you.0
-
One of those two valves leaks and, if you have closed the feed to the auto water feeder and it still fills, it is most likely the bypass Manual feed) valve. Is it a ball valve or some other type of shut-off? It could have some crud built up in the seat that prevents the valve from completely seating.0
-
I believe the manual feeder is a ball valve with a lever handle. Will post a picture of that tonight as well.0
-
Sorry for the delay posting pictures. Any one seeing these side ways?
0 -
One of your valves is leaking by. See if the pipe to the auto feeder feels colder that the one feeding the boiler. The ball valves are less likely to leak by than the stop valve but the ball valve in this instance seems more likely unless the auto feeder is also leaking by0
-
Based on these pictures, I see only the bypass valve is a ball valve. I would say the valve that feeds the water feeder is leaking and the solenoid valve in the water feeder isn't fully seating either.0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements