Condensation Fault with Carrier Infinity Touch Control
obx_guy
Member Posts: 1
I have a 59MN7A condensing furnace that is controlled by infinity touch control using the 4 wire com bus.
I have installed a Diversitech condensation pump that has a set of contacts to to shutdown the system rated at 1 amp at 24V if the water backs up. I also wanted to put a switch in the drain line itself that didn't rely on power. Is there a way to interface this with the system to get it to shut down the system. I had thought about putting it in line with the door switch but that is 120V and not the best way of doing it. You would think that there would be a way to input a fault signal to the system... Hard to believe that they have all this capability and never thought about providing external signal inputs for external problems.
I have installed a Diversitech condensation pump that has a set of contacts to to shutdown the system rated at 1 amp at 24V if the water backs up. I also wanted to put a switch in the drain line itself that didn't rely on power. Is there a way to interface this with the system to get it to shut down the system. I had thought about putting it in line with the door switch but that is 120V and not the best way of doing it. You would think that there would be a way to input a fault signal to the system... Hard to believe that they have all this capability and never thought about providing external signal inputs for external problems.
0
Comments
-
You can have NC contacts in series with the C or D wires that are going to the the controller/thermostat.
That's how I do it, and tell the customer is the screen goes blank to call asap.0 -
Yes it's discussed in the Infinity thermostat instructions, I did this with a Bryant a couple months ago.0
-
You can wire the pump contacts to R and G terminals, then enable the G terminal in installers set-up of the controller. When 24v is sensed at G, a fault is detected and shut down the unit.0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 915 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements