Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
Problems w New MEPCO VST's
Billurbs
Member Posts: 5
We recently replaced about 1,000 VST steam traps in a high rise building. (over the summer) Now, come heating season, we're finding that about 20% of the new traps elements are failed open. This is pressurizing our returns lines and preventing steam circulation, particularly at the upper floors. Anyone else experiencing this problem?
Despite MEPCO's claim that 100 % are tested, we're finding high failure rates.
Despite MEPCO's claim that 100 % are tested, we're finding high failure rates.
0
Comments
-
Did you replace the entire trap or just the element?
We use the same body at the Mepco VST but machine them out for our cage unit. I haven't heard anything about that specific trap having problems.
I'd be happy to test some if you like see if we can pinpoint the issue.Peter Owens
SteamIQ0 -
Entire Trap - Between two unions0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements