Crown Mega Stor Indirect or Velocity Mega Stor II ?
flat_twin
Member Posts: 354
Any thoughts on the Velocity Mega Stor 2 indirect water heater? It appears to be the next generation of the Crown Mega Stor. I read it's made with 444 stainless steel and found this in the manual regarding chloride count...
"Not covered under warranty.. Any indirect‐fired water heater that has potable water with the following characteristics: chloride levels in excess of 80 PPM, measurable amounts of any compound containing chlorine, or PH less than 6.0 or greater than 8.0."
Should I have my municipal water tested beyond a hot tub dip strip? It's very good water with no taste or smell of chlorine.
I plan to retire our 23 year old Rheem electric water heater next summer and take advantage of the new NG modcon boiler.
Thanks!
Mark
Velocity Mega Stor II info
http://www.velocityboilerworks.com/documents/MegaStor_II_Manual.pdf
"Not covered under warranty.. Any indirect‐fired water heater that has potable water with the following characteristics: chloride levels in excess of 80 PPM, measurable amounts of any compound containing chlorine, or PH less than 6.0 or greater than 8.0."
Should I have my municipal water tested beyond a hot tub dip strip? It's very good water with no taste or smell of chlorine.
I plan to retire our 23 year old Rheem electric water heater next summer and take advantage of the new NG modcon boiler.
Thanks!
Mark
Velocity Mega Stor II info
http://www.velocityboilerworks.com/documents/MegaStor_II_Manual.pdf
0
Comments
-
Yes, test your water or see if the water provider has that info.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
DelCo water quality info from their website.
pdf link Go to the bottom for the numbers. Chloride levels not given so I'm contacting them for more info
http://delcowater.org/wp-content/uploads/2015/07/2015CCReady.pdf0 -
Maybe take a sample and have it tested locally. Or send it to Rhomar Water for testing. It just needs to be tested specific to hydronics, not drinking quality.
Ph, hardness, TDS, chlorides are the main ones. The water needs to be compatible with all the metals in the system, not aggressive or too many scale forming minerals.
Here is a link with info about the various tests.
http://www.rhomarwater.com/assets/pdf/literature/Water-Test-Request-Form.pdfBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
A DelCo water tech called and said they're not required by the EPA to test for chlorides so they don't and unless I have a water softener, chloride levels are so insignificant it's not an issue.
Looks like I'll have to go for an independent test if I want a solid number on chlorides.
FWIW, The boiler installer flushed tested and treated the hydronic water with Sentinel X100 in November0 -
As you have discovered, the tank and boiler manufacturers are sure concerned about chloride levels. They seem to be on the increase in out public and private water systems, just a heads up.flat_twin said:A DelCo water tech called and said they're not required by the EPA to test for chlorides so they don't and unless I have a water softener, chloride levels are so insignificant it's not an issue.
Looks like I'll have to go for an independent test if I want a solid number on chlorides.
FWIW, The boiler installer flushed tested and treated the hydronic water with Sentinel X100 in November
The levels can change depending on the water table, rains, surface contaminants, etc. It doesn't hurt to test from time to time, just as the city is required to do.
Public water providers are concerned more with health of the people, not the health of your components. It's possible that those EPA requirements may get watered down.
You are wise to use a hydronic water treatment. One key component is the film provider which puts a thin, micron thick layer on the bare metal to help protect it from aggressive fluids.
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
OK, I have the test results and they indicate Chloride is 14 mg/L. I believe that's essentially the same as 14 ppm, well under the 80 ppm requirement for warranty coverage of a stainless steel indirect. Chlorine in my water is 1.38 ppm.
I noticed Weil McLain also specified in their warranty docs that Chloride and Chlorine levels must be less than 80.
I see the WM indirects are no longer tank in tank but a coil type heat exchanger and they've added an anode rod.
Are any of you using or have installed this latest version WM indirect? Good unit? Any problems? I intent to get a price from my heating contractor who uses WM products so I'm asking about WM as well as any suggestions from you guys about other brands.
Honestly, I'm tempted to give this a go myself with the help of my neighbor who's a plumber by trade. I have studied the diagrams that came with the WM Eco boiler which cover adding an indirect WH.
I'm a retired Telco technician so wiring doesn't scare me and I've sweated copper in my past.
0 -
I would like to hear from anyone who owns or has installed the MS II with the 444 stainless steel. Have been unable to find any info on this model other than from the manufacturer.0
Categories
- All Categories
- 85.8K THE MAIN WALL
- 3K A-C, Heat Pumps & Refrigeration
- 50 Biomass
- 419 Carbon Monoxide Awareness
- 91 Chimneys & Flues
- 2K Domestic Hot Water
- 5.2K Gas Heating
- 93 Geothermal
- 150 Indoor-Air Quality
- 3.4K Oil Heating
- 59 Pipe Deterioration
- 920 Plumbing
- 5.8K Radiant Heating
- 374 Solar
- 15K Strictly Steam
- 3.2K Thermostats and Controls
- 50 Water Quality
- 40 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements