Max venting needed for 3/4 inch main antler
Options
Motorapido
Member Posts: 314
I'd like to vent my main at the same capacity that it would vent if no vent were attached to the fitting and the pipe were wide open. I have two Barnes and Jones Big Mouths on an antler that joins the main with a 3/4 inch nipple. My single-pipe, parallel flow steam system typically operates between about 6 and 11 ounces of pressure, measure on a brand-new 0 to 3 psi gauge. Do I need to add any venting to move the maximum amount of air through that 3/4 fitting, or are the two Big Mouths currently allowing all the air to vent at the same capacity that air would vent if that 3/4 fitting were wide open?
0
Comments
-
A 3/4" pipe will vent at 9.5 CFM @3 ounces of pressure. The Bigmouths vent at 3.6CFM @ 3 ounces. Technically you could add another Bigmouth and get about 66% of its capacity but the amount of time you save by doing that simply doesn't justify spending the money. If you took off a good Gorton #2 vent to put the Bigmouths on, you certainly can put one of those back on the antler with the two Bigmouths to get the full venting capacity of te 3/4" pipe. The Gorton vents at 2.2 CFM at 3 ounces of pressure.1
-
Thanks, Fred. The vent I removed and replaced with the Big Mouths was ancient and stuck shut, so I figure I'll bite the bullet and buy another Big Mouth, which will give me more venting capacity than the 3/4 inch pipe will pass. They sure are pretty to look at, and when I'm done, I'll know I've gone the extra mile. Thanks for the info.0
-
@Motorapido , LOL, I like looking at mine too!0
Categories
- All Categories
- 87.3K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 429 Carbon Monoxide Awareness
- 120 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 114 Geothermal
- 166 Indoor-Air Quality
- 3.7K Oil Heating
- 77 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.7K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements