steam trap size
Options
Ralphie513
Member Posts: 6
if i have a stainless steel steam kettle requiring 120 lb/hr with 6-7 lbs steam supply and the condensate return from the trap to the pump feed is near horizontal what would be the correct size trap? is 2300 lb/hr correct with a 3x safety factor?
0
Comments
-
lb./hour x safety factor=120 x 3=360 lb/hour load on trap.
Then consider pressure differential across trap.
do you always have 6psi at the equipment inlet? Or is there a control valve between the supply steam and the steam kettle?
If you have a control valve size the trap for 360 lb/hr with 1/2psi pressure differential across the trap.
With no control valve size the trap for 6psi differential
Both the above examples assume that there is 0 psi pressure (no back pressure) in the condensate return.
Either way a Watson McDaniel 3/4" F & T trap is rated at 440 lb/hr at 1/2 psi diff would do it.0 -
yes it has a valve and the pressure is not always that high, only during heat up then backed off a couple lbs0
-
3/4" 15PSI trap is more than enough. We make traps for many OEM jacketed kettle companies like Blodgett, Manitowoc, Market Forge, Groen and they use a 1/2" radiator trap or one of our compact traps which have far less capacity.Peter Owens
SteamIQ0
Categories
- All Categories
- 87.3K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 429 Carbon Monoxide Awareness
- 120 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 114 Geothermal
- 166 Indoor-Air Quality
- 3.7K Oil Heating
- 77 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.7K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements