Lwco
happydave
Member Posts: 79
Piped and wired in a Burnham pin7 with a hydrolevel cg400 yesterday, turn power on , leds on lwco flash for a quarter of a second then nothing. 24 volts in and out of lwco. No leds, doesn't even start to cycle, bad lwco? bad ground? Going back this morning to trouble shoot and finish up, any ideas before I dig into it. Thanks Dave
0
Comments
-
If you have 24V on the burner output terminal, and the boiler water is above the probe, the LWCO is OK. I see in the pic the pressuretrol and stack damper are not hooked up, were they hooked up when you tried to fire it?
How about the blocked-flue switch?
The Independence boilers have isolation relays- the thermostat operates the relay which closes the burner circuit. Is this relay working?All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Ha, yeah all connected, just wanted to show the piping. Why no leds? Power should leave the transformer to lwco then to the relay or the other way around? Didn't dig into it as they had supplement heat and I long day. Thanks0
-
Sorry about the 3" coupling but my die head can't thread that short.0
Categories
- All Categories
- 86.4K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 94 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 925 Plumbing
- 6.1K Radiant Heating
- 383 Solar
- 15K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements