TACO Pump or controller bad?
dquelch
Member Posts: 1
Novice homeowner here who doesn't plan to take on more than he can handle, but I would like to attempt to diagnose the issue before calling in a professional.
I have a 4 zone hot water system fired from an oil burner. One of the zones (zone 3) is for a radiant floor system on my ground level. I tested this system back in October to ensure it was working properly. Though when calling for heat from the thermostat, it did take a while for the circulator to kick in, it did eventually.
Fast forward to this weekend. I usually keep the radiant floor thermostat at 65 degrees then supplement with forced hot air when needed. I noticed this weekend that my ground floor temperature was at 60 degrees (what I keep the forced hot air at when not in use) which told me the radiant floor heating was not operational. Radiant floor thermostat indicated it was calling for heat. I checked the controller unit and the light for zone 3 was not lit, nor was the exit pipe from the circulator hot indicating the circulator was not (nor had been) running. I shut the thermostat off, then on again to see if the furnace would kick in and the controller would light up. Nothing. The other three zones work fine with regards to the controller light and the circulators kicking in, just not the zone that the radiant floor is on. I swapped out the thermostat this morning and same result.
The controller is a TACO SR504
The circulator pump is a TACO OOR-MSF1-IFC
So my questions are:
1. Is it possible for a single relay in a controller box to be bad?
2. Does a controller zone's light only light up if the circulator is running?
3. Is there a way to manually start a circulator to test it's functioning?
4. If a zone intermittently works, what is that a sign of?
Thank you!
Dennis
I have a 4 zone hot water system fired from an oil burner. One of the zones (zone 3) is for a radiant floor system on my ground level. I tested this system back in October to ensure it was working properly. Though when calling for heat from the thermostat, it did take a while for the circulator to kick in, it did eventually.
Fast forward to this weekend. I usually keep the radiant floor thermostat at 65 degrees then supplement with forced hot air when needed. I noticed this weekend that my ground floor temperature was at 60 degrees (what I keep the forced hot air at when not in use) which told me the radiant floor heating was not operational. Radiant floor thermostat indicated it was calling for heat. I checked the controller unit and the light for zone 3 was not lit, nor was the exit pipe from the circulator hot indicating the circulator was not (nor had been) running. I shut the thermostat off, then on again to see if the furnace would kick in and the controller would light up. Nothing. The other three zones work fine with regards to the controller light and the circulators kicking in, just not the zone that the radiant floor is on. I swapped out the thermostat this morning and same result.
The controller is a TACO SR504
The circulator pump is a TACO OOR-MSF1-IFC
So my questions are:
1. Is it possible for a single relay in a controller box to be bad?
2. Does a controller zone's light only light up if the circulator is running?
3. Is there a way to manually start a circulator to test it's functioning?
4. If a zone intermittently works, what is that a sign of?
Thank you!
Dennis
0
Comments
-
Jumping out thermostat connections R &W for a validated demand is a good way to start diagnosing problem. This simple exercise will determine if it's a thermostat, wires from thermostat to control, or SR504; it could be circulator too. The circulator should run as soon as R & W close. If it doesn’t run, it could be a bad pump. You can apply 120 volts directly to pump too, if you want to see if it’s a bad pump. If you have an amp meter, you should measure close to nameplate amps. If the amp reading is 1.5 times nameplate, it would indicate locked rotor condition, and cartridge should be replaced you can contact Taco tech support at 401-942-8000 and ask for tech support. It would be helpful if you have access to control when trying some troubleshooting exercises.Joe Mattiello
N. E. Regional Manger, Commercial Products
Taco Comfort Solutions0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements