Lasrs ebp 175 no hot water
Options
ArchimoreHorie
Member Posts: 27
Hi. I have a lasrs endurance ebp 175
First I have a LO. I change the igniter
Then I have heat but no DHW. I replace the flow switch. Still no hot water. I replace the pump. Water goes from hot to warm to cold in less than 4 minutes. My heat work fine.
Please help me. Thanks Archie
First I have a LO. I change the igniter
Then I have heat but no DHW. I replace the flow switch. Still no hot water. I replace the pump. Water goes from hot to warm to cold in less than 4 minutes. My heat work fine.
Please help me. Thanks Archie
0
Comments
-
Check anti condensing valve.0