Can PVC intake and exhaust be routed to the outside concentric vent through a joist cavity which will be enclosed by drywall?

Comments

  • Mad Dog_2
    Mad Dog_2 Member Posts: 7,500
    In NY, it isn't allowed anymore. CPVC or polypropylene or SS. Check with the manufacturers requirements. Mad Dog
    gggnbcPaul S_3
  • lchmb
    lchmb Member Posts: 2,997
    In NH you cannot use pvc on boilers.
    gggnbckcopp
  • Steamhead
    Steamhead Member Posts: 17,358
    PVC is not UL approved for venting combustion products, and Code authorities are finally taking notice of this. CPVC is not UL approved for this purpose either. Even if PVC or CPVC is still permitted in your area, I wouldn't use it. Use stainless steel, or something like what Centrotherm sells:

    http://www.centrotherm.us.com/

    You should be able to find required clearances in the various manufacturers' instructions.

    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
    gggnbc
  • adambnyc
    adambnyc Member Posts: 260
    Interesting. I vented my tankless hot water heater with PVC as per the manual instructions. In fact the Heater has intake/exhaust are PVC hubs direct from the factory. Different rules for hot water heaters? My town inspector passed me without issue.
  • Solid_Fuel_Man
    Solid_Fuel_Man Member Posts: 2,646
    Some (maybe most) manufacturers will list pvc, cpvc, polypropylene, and stainless as accepted venting materials in their literature. The pipe manufacturers do not approve their pipe for combustion venting, just dwv of sewer. It's been a grey area for quite awhile.

    That said there are thousands, maybe hundreds of thousands of installs with pvc venting...
    PVC and CPVC have the (in my opinion) advantage of being solvent welded and essentially made into a continuous piece. Polypropylene, while better material has the (in my opinion) drawback of relying on gaskets for joining. Same with stainless. If those two materials could be made continuous there would be a bullet-proof systems.
    Serving Northern Maine HVAC & Controls. I burn wood, it smells good!
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 16,364
    @Solid_Fuel_Man ,@Steamhead.

    I am not advocating PVC use but my understanding is that there is only one manufacturer that has PVC that is listed for combustion venting.

    Ipex #636 is available in PVC & CPVC and is approved for venting.

    There are issues with pvc so I think it will slowly go away as a vent material
  • Paul S_3
    Paul S_3 Member Posts: 1,277
    edited January 2017
    I once seen a partially melted pvc exhaust on a rheem tankless water heater....I found out a scaled/dirty heat exchanger can cause this....less heat transfer to the water created really high flue temps....ive used cpvc....but now only polypropelyne products made from centrotherm.... and in nyc they will fail you immediately if you use pvc
    ASM Mechanical Company
    Located in Staten Island NY
    Servicing all 5 boroughs of NYC.
    347-692-4777
    ASMMECHANICALCORP@GMAIL.COM
    ASMHVACNYC.COM
    https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company
  • Steveheat
    Steveheat Member Posts: 1
    Peerless allows the use of Scd.40 PVC. On their Pure fire condensing boilers.
  • Jason_13
    Jason_13 Member Posts: 305
    IPEX 636 I believe is only certified in Canada
  • Steamhead
    Steamhead Member Posts: 17,358
    adambnyc said:
    Steveheat said:

    Peerless allows the use of Scd.40 PVC. On their Pure fire condensing boilers.

    adambnyc said:

    Interesting. I vented my tankless hot water heater with PVC as per the manual instructions. In fact the Heater has intake/exhaust are PVC hubs direct from the factory. Different rules for hot water heaters? My town inspector passed me without issue.

    Doesn't matter if the boiler manual allows it- if it's against Code in your area, you can't use it. Some inspectors will pass it now, but that will change as Codes get updated.
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • hot_rod
    hot_rod Member Posts: 23,225
    Steamhead said:

    adambnyc said:
    Steveheat said:

    Peerless allows the use of Scd.40 PVC. On their Pure fire condensing boilers.

    adambnyc said:

    Interesting. I vented my tankless hot water heater with PVC as per the manual instructions. In fact the Heater has intake/exhaust are PVC hubs direct from the factory. Different rules for hot water heaters? My town inspector passed me without issue.

    Doesn't matter if the boiler manual allows it- if it's against Code in your area, you can't use it. Some inspectors will pass it now, but that will change as Codes get updated.
    Good point, getting the approved products in the codebooks is the first start.

    Unfortunately not all jurisdictions adopt or use the most current codebooks. In my area we still use 2012 version! until the board votes to accept a newer version.

    It would be nice to see the final chapter to this PVC venting issue.
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • Henry
    Henry Member Posts: 998
    S636 PVC is the same pipe as sch 40 PVC. The colour is different and the labelling is different. There are standards to manufacture PVC SCH 40 pipe and S636. The physical components to make the pipe is essantially the same. In 2007 when I was in Europe and missed our annual code meeting, Ontario passed a motion to have the venting material aprooved as S636. They claimed that IPEX made the pipe. This was not true. It took over a year to get the new labelling and colour aprooved. We, as mechanical contractors vent with S636 up to and including 6 inch if it is written in the I & O manual. The Raypack condensing boilers are very specific for the number of elbows and material as well as vent lenght. HTP & Lochinvar are the easiest to vent. On the largert condensing boilers we go with AL24C.
  • j a_2
    j a_2 Member Posts: 1,801
    I have seen yellowing of some pvc vented boilers and furnaces...Not a pvc guru, but maybe someone will chime in on it...Who knows better.