Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.

Ray-tec radiant heater

Options
I have a Ray-Tec radiant heater and it has 4 cells. theres flame coming out of two cells. none of the cells get red either.

Comments

  • JUGHNE
    JUGHNE Member Posts: 11,062
    Options
    Do you have a picture of this event?
  • Abracadabra
    Abracadabra Member Posts: 1,948
    edited January 2017
    Options
    1. Excessive gas pressure
    2. Defective regulator
    3. Lack of combustion air
    4. Cracked/damaged ceramic
    Don't run it until it is corrected/serviced
    JUGHNE
  • Threefingers
    Threefingers Member Posts: 3
    Options
    No Pics, But I think it might be set up for propane, and I'm using NG. I friend at work suggested I look at the orfice and see what size it is. I may need to get smaller ones for each cell.
  • Mark Eatherton
    Mark Eatherton Member Posts: 5,853
    Options
    That combination usually reduces the input. Doing the opposite (running propane through natural gas orifices and regulators) will over fire the unit.

    In addition to changing out the orifices, you'd also have to make a spring change to the regulator.

    Contact the manufacturer for specific instructions and appropriate parts. Have the model number and serial number available before you call.

    ME

    There was an error rendering this rich post.