Replacing Taco 007 with a variable circulator
pesiroil
Member Posts: 1
hello, I am an electrician and was hoping I could get some advice from yall. Currently have a gas fired hot water system with 4 zone valves and a taco 007-bf5-j circulator.
I started having issues a couple weeks ago with zero water flow through my basement zone and was positive it was an air-lock in the pipes, after many many attempts of getting this airlock out and failing i decided it could be another problem.
i took an amp reading on the circulator and its pulling 1.1amps and the nameplate says .76amps. Out of the three zones the basement is the most complicated and creates a larger head loss then the other two zones. The other three zones are very close in proximity and straightforward zones which apparently the circulator had no issues with.
I could do the easy fix and just replace it with the same circulator, but im reading up on variable speed circulators im willing to pay the extra for the right cireculator and wanted to know if i would have any issues. I also have an aquastat controller that my current circulator is wired to is it the same type of wiring or is there a a type of lowvoltage control wiring needed?
Also delta T or delta p, and is there any variable circulators you would recommend?
I started having issues a couple weeks ago with zero water flow through my basement zone and was positive it was an air-lock in the pipes, after many many attempts of getting this airlock out and failing i decided it could be another problem.
i took an amp reading on the circulator and its pulling 1.1amps and the nameplate says .76amps. Out of the three zones the basement is the most complicated and creates a larger head loss then the other two zones. The other three zones are very close in proximity and straightforward zones which apparently the circulator had no issues with.
I could do the easy fix and just replace it with the same circulator, but im reading up on variable speed circulators im willing to pay the extra for the right cireculator and wanted to know if i would have any issues. I also have an aquastat controller that my current circulator is wired to is it the same type of wiring or is there a a type of lowvoltage control wiring needed?
Also delta T or delta p, and is there any variable circulators you would recommend?
0
Comments
-
https://www.taco-hvac.com/products/variable_speed_products/vr2218/index.html
I'm a fan of a nice delta t pump myself. I've used them in many applications and have heard nothing but good savings...0 -
The ECM pumps run 120V same as the 007. Easy to swap out, no additional controls/wiring. Zero issues for you on that front.
0 -
007, the most popular of 00 family of pumps, has a relatively flat curve, is readily availability, robust, and engineered for easy replacement of cartridge assembly when it fails. Your amp reading of approximately 1.5 X nameplate indicates a locked rotor condition. Replacing the cartridge 007-042RP is the easiest, and least costly fix.
However, if you’re interested in the latest and greatest high efficiency innovations, Taco 007e should be considered. Its performance is equal to 007, but uses up to 85% less electricity making it a great economical upgrade to your system. 007e constant pressure curve makes it ideal for a multi zonevalve dynamic system, reducing velocity, erosion, and noise.
Attributes; ECM technology delivering high efficiency, Bio barrier minimizes fouling, Integral flow check, and Sure-start technology which continuously jogs pump shaft to prevent locked rotor, all of which makes 007e a wise choice. Hopefully this helps you make an informed decision. For your convenience, I provided a link to catalog.
http://www.taco-hvac.com/uploads/FileLibrary/100-123.pdf
Joe Mattiello
N. E. Regional Manger, Commercial Products
Taco Comfort Solutions0 -
pesiroil,
I am assuming that this system has worked for a long time already with the existing 007?
If so, the reason you may not be getting any heat in the basement is because of gravity flow. The basement loop is below the boiler whereas the other zones upstairs are getting heat, but probably not at the same rate as before. The zone valve opens and hot water will naturally rise.
The amp reading does indicate that the rotor is not rotating and is locked. The 007e as Joe mentioned above would be perfect for your system if the original 007 worked just fine in the past.
If what you are saying that the developed head in the basement zone is larger than what the 007 or the 007e can handle, thrn I would look into the VT2218, Delta T circulator. It can handle higher head projects and wires the same except for a couple of temperature sensors.
Dave H.Dave Holdorf
Technical Training Manager - East
Taco Comfort Solutions
0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements