Burner cycles
Neild5
Member Posts: 171
Hi again. I would have asked the guy who installed the boiler this but he is in the hospital. There are 3 Dundick model 500 base units tied together, the center and right units are acting normal, the left unit after running for a while will shut the gas off for 2-3 seconds every 2 minutes or so. Is this something serious or can it wait until he is healthy?
0
Comments
-
-
It can wait as long as the boiler has enough capacity with the two burners. I would shut the electrical off and disconnect the wires to the gas valve and tape them up. Also shut off the gas cock to the offending burner.0
-
not sure if this is related to your problem, but that header doesn't look anything like what dunkirk recommends.
pretty sure you don't have the minimum height for the riser before you hit the header. Sounds like an issue with the ignition control proving flame carryover. View burner and see if you note an issue with the flame. Could be an erratic ground. Verify pilot flame covers the flame rod. Could be a failing ignition module.
if that was my boiler, i'd demand he clean up the electrical. that looks terrible.0 -
> @Abracadabra said:
> not sure if this is related to your problem, but that header doesn't look anything like what dunkirk recommends.
> pretty sure you don't have the minimum height for the riser before you hit the header. Sounds like an issue with the ignition control proving flame carryover. View burner and see if you note an issue with the flame. Could be an erratic ground. Verify pilot flame covers the flame rod. Could be a failing ignition module.
>
> if that was my boiler, i'd demand he clean up the electrical. that looks terrible.
Question, the piping coming out of the boiler is 3 inch, on the left side it goes up at 45 degrees to a horizontal pipe and then has 2 risers to a large header where the right riser joins it before the main line comes off the header. Since the large header is definitely high enough, will the two lower horizontal runs cause any problems?0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 89 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements