Secondary loop question

Gooch
Gooch Member Posts: 62
Does it matter in a secondary loop how close the tees are in the supply side that feed different zones?

Comments

  • cnmdesign
    cnmdesign Member Posts: 103
    edited November 2017
    :/ comment removed.
    Combat Veteran owned, Final Salute LLC on FaceBook & Twitter.
    www.afinalsalute.com
  • delta T
    delta T Member Posts: 884
    are we talking about the closely spaced tees for hydraulic separation, or a manifold on the secondary side after hydraulic separation? If the latter, then no it shouldn't matter. If you are talking about closely spaced tees for hydraulic separation, then really just as close as possible, and not more than 12"