Honeywell RTH6580WF
LionA29
LionA29 Member Posts: 255
Thermostat set point is 70° and room temp is 70°. Turned Tstat up to 71°, after a minute room temp went to 71°. Raised to 72°, after a minute room temp went to 73°.
Seems like for some reason the Room temp is going up with the set point settings on the Tstat. Room temperatures hasn't change with the 3° increase.Is this a defective tstat or anyway to calibrate it?
  • Big Ed_4
    Big Ed_4 Member Posts: 3,364
    Are you comfortable ... Forget the numbers....
  • LionA29
    No.
    The actually temperature in the room doesn't change but the reading on the thermostat changes.
  • Fred
    Fred Member Posts: 8,542
    That ain't right @LionA29 . I raise my tstat a degree and I hear it click and the boiler kicks on.
  • LionA29
    edited December 2016
    @Fred
    Mine does that, but it can't satisfy the thermostat in a 1 minute?!
    3° jump and the boiler was running about 3 minutes then it satisfies but the actual room temp still remains the same.
    The chill in the room still remains.
  • Fred
    LionA29 said:
    @Fred
    Not unless the tstat is lying about how much it is overshooting the actual set point (which some of them do). What does a thermometer say, near the tstat?
  • LionA29
    @Fred
    Thermometer reads 70° when thermostat reads 73°
  • Fred
    Then something isn't right with that Tstat.
  • LionA29
    In less than 2 mins Tstat room temp jump.
  • Fred
    What's behind that wall? Did you fill the hole for the wires with insulation?
  • LionA29
    @Fred ,
    Yes for that same reason I made sure wall was ceiled and insulated.
  • LionA29
    Replaced Tstat with the simplest and it works perfect. No more WiFi and setbacks. Boiler cycles better and temps are way better!
    Thank you @Fred for your time and help.
  • Fred
    Glad it's working @LionA29 ! Hope you and the family have a Great Holiday!
    LionA29
  • LionA29
    Thank you and to you as well!