baseboard hot water off steam boiler - stopped working after 'repair'
mike212
Member Posts: 50
I have baseboard hot water heat in the basement that runs off the steam heating oil fueled boiler. Water temp is set to 170 degrees.
I had work done in the basement and the GC replaced the old baseboards with new ones. First he turned off the water supply, cut open the baseboard, and drained them. Then cut out the old baseboard heaters and installed the new ones.
The water supply was then turned back on.
Since then heat through the baseboards has been weak to not working. (I'm not 100% sure this heat was working properly before - we just moved in recently and never used this baseboard heat although I think we tested it at one point but I'm not 100% certain).
As an example, today I turned on the baseboard heat and can hear the sound of the boiler or something near the boiler pumping water once the thermostat for the baseboard is triggered. 3 hours later the baseboards are still cold. I turned off the thermostat and can hear that sound stop right away.
Any ideas on what I can try to get this working? The GC is not helpful on this and says its a boiler issue, the piping he connected is working fine.
I had work done in the basement and the GC replaced the old baseboards with new ones. First he turned off the water supply, cut open the baseboard, and drained them. Then cut out the old baseboard heaters and installed the new ones.
The water supply was then turned back on.
Since then heat through the baseboards has been weak to not working. (I'm not 100% sure this heat was working properly before - we just moved in recently and never used this baseboard heat although I think we tested it at one point but I'm not 100% certain).
As an example, today I turned on the baseboard heat and can hear the sound of the boiler or something near the boiler pumping water once the thermostat for the baseboard is triggered. 3 hours later the baseboards are still cold. I turned off the thermostat and can hear that sound stop right away.
Any ideas on what I can try to get this working? The GC is not helpful on this and says its a boiler issue, the piping he connected is working fine.
0
Comments
-
This will help: https://heatinghelp.com/systems-help-center/how-to-run-a-hot-water-zone-off-a-steam-boiler/Retired and loving it.-1
-
Thanks Dan. Problem solved. The baseboards were filled with air. I used a garden hose from the hot water heater to fill in the air with water.0
-
I figured. Tell the GC he needs to learn more. I don't like the way he's treating you.Retired and loving it.0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements