Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
Radiator bleeder question
kman_2
Member Posts: 2
Hi guys, I just installed an old cast iron hot water radiator. The placement of the air bleeder seems suspicious to me. I also uncovered a plug in top right corner, which may or may not be where the bleeder should be. I have more questions but I will leave it at this for now. I would like some thoughts on the image. thanks
0
Comments
-
It must have been used for steam in it's previous life. That is the location of the vent on a steam system. You want to plug that and use the bleeder location you found at the top.1
-
Thanks KC, that makes sense0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements