Heater not working
michelle_10
Member Posts: 5
in Gas Heating
We have a brand new home with brand new hvac unit. The heater will not blow hot air. Have no issues with the ac. We've done the following trouble shooting:
- unit has a brand new filter
- Pilot-less unit and it is running. Not pilot issue or breaker issue
- Gas to unit is on position
- Thermostat is set to heat and fan auto
- When fan set to on, it does blow cold air. Not duct blockage
Not sure what else we can try. The home has two units and the other one is working just fine in heat mode.
- unit has a brand new filter
- Pilot-less unit and it is running. Not pilot issue or breaker issue
- Gas to unit is on position
- Thermostat is set to heat and fan auto
- When fan set to on, it does blow cold air. Not duct blockage
Not sure what else we can try. The home has two units and the other one is working just fine in heat mode.
0
Comments
-
Might be a safety has tripped, what make and model is it? Pictures might help.
BobSmith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
Vaporstat with a 12oz cut-out and 4oz cut-in
3PSI gauge0 -
Need model and flash code from the control. Open up the front cover, the control should be flashing a red LED. Count the number of flashes. They will repeat.0
-
Trane Xb Model 4txcb031bc3hcba
3 red flashes0 -
As I was down here getting the info, the unit is running for about 2 minutes and then turning off for 30 seconds.0
-
It sound like the flame sensor isn't working but someone will know for sure what the 3 flashes indicates.0
-
3 Flashes — Draft pressure error – possible problems: a) venting problem, b) pressure switch problem, c) inducer problem.
You need to call a service tech0 -
Sounds like it's an "above the homeowners head" problem? Hahahahaha Or does it just sound more technical than it is? Is this normal for a unit that's not even a year old?0
-
-
Thanks everyone for all the quick advice. Thankfully it's an unusually warm November here in Kansas. We're calling a service tech tomorrow. Until then, it's fireplace and gloves for us!0
-
- Check the intake for blockage, the exhaust for blockage
- Check the inducer
- Pressure switch failure is at the bottom of the list.
0 - Check the intake for blockage, the exhaust for blockage
-
Also, check all the condensate lines for blockage. Particularly the line coming from the bottom, exit of the secondary heato exchanger. If it gets blocked, the level of condensate inside can rise to the point of blocking the pressure switch tube attachment point. That will cause this same error. Also check all the "pressure switch" tube attachment points. Over the years they can start leaking as the latex or rubber hardens and cracks. Sometimes you can cut them back an inch and reinstall them, wrapping the attachment point with a small zip tie.1
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements